reTerminal-DM touchscreen unstable when powered from industrial 24 V supply, works only when touching chassis

I am using a reTerminal DM with injection molding machine and facing unstable capacitive touch behavior.

Symptoms:

  • Screen randomly zooms in/out

  • Touch position shifts

  • Touch becomes stable only when I physically touch the reTerminal chassis with my hand

  • Issue appears when powered from Mean Well mdr-60-24 power supply.

This suggests a grounding or common-mode noise issue affecting the capacitive touch controller.

Power setup

Power supply used:

Mean Well MDR-60-24 (DIN-rail SMPS)

Connections made:

  • L/N connected to machine single-phase supply

  • +24 V / −24 V connected to reTerminal DM

  • V− bonded to panel PE

  • reTerminal chassis bonded to panel PE

  • MDR-60-24 FG bonded to panel PE

Despite these connections, issue persists.

Measurements

Measured AC voltage between:

MDR-60-24 V− and panel PE ≈ 60 V AC (before grounding changes)

After bonding FG and V− to PE, behavior improved slightly but touchscreen instability still remains.

Touch becomes stable immediately when:

I touch chassis with my hand

which suggests missing reference stabilization or high common-mode noise in cabinet environment.

Machine environment

Installation is inside an injection molding machine panel containing:

  • hydraulic motor contactors

  • possible VFD drives

Cable length between PSU and reTerminal is short (<2 m).

Tests already performed

Tested:

  • bonding V− to PE

  • bonding FG to PE

  • bonding chassis to PE

  • verifying continuity of panel earth

Questions

  1. Is reTerminal DM known to require isolated supply in industrial control panels?

  2. Does Seeed recommend grounding output negative to PE or keeping it floating?

  3. Are there any official EMC mitigation guidelines for capacitive touch stability in noisy cabinets?

  4. Has anyone successfully deployed reTerminal DM with injection molding or CNC panels without isolated DC-DC stage?

Hi there,

SO, on the IO/ panel isn’t there an ISO/GND pin , used on the canbus often too.
it’s the dedicated isolated pin on the reTerminal, I was under the impression. I think also a post of another maker using it similar too , the isolation for power supply GND (noise) issue for your use case FAIK.

HTH
GL :slight_smile: PJ :v:

Hi @PJ_Glasso

I tried following connection: Injection Molding panel earth to Negative of the meanwell MDR-60-24 power supply output and ran a short wire to connect panel earth to reterminal-dm earth [Above the power supply port]

As per your suggestion, should I connect injection molding machine panel earth to GND_ISO?

Because this earthing issue is causing touch screen instability [zoom in/out, ghost touch] and is not usable at all. Should I also reach out to seeedstudio team for the same?

Hi there,

Ok, YES absolutly . Connect it and report back, You can’t hurt anything so no worries there.
if possible can you measure your power supply AC ripple component. if it’s too noisy , find a higher working voltage CAP and nothing huge 20 uf. see if it lowers it a bit in the meter, (ac settings) checking the DC supply. note the reading, add the cap ..note the reading. Any change if so try the reTerminal again.

HTH
GL :slight_smile: PJ :v:

I have had some super crazy noise enviro’s before, one was a motor for an overhead crane… when that thing kicked into gear and moved , it would spike the AC around the whole neighborhood it seemed :grin: We added Heavy Isolation and split filtered the mains supplied to it. added some additional CAPs to the power supply for the servos and MMI display power legs, and life was good again. :crossed_swords:

Hi @PJ_Glasso

There are some improvements from last time, as stated earlier reterminal DMs were connected to total 19 injection molding machines and is used for real-time data acquisition from injection molding controllers and HMIs using LAN and RS485 (In few controllers).

Earthing was refreshed and connections were re-checked, BUT the bad news is still there was issue with touch sensitivity with ghost touches, zoom etc. For a quick test I also removed AC power supply from meanwell SMPS and connected battery UPS and still there was this touch issue. I also replaced temporary omron power supply with meanwell one but this didn’t help.

As you suggested I tried reading AC ripple on power supply (SMPS) output but my UNI-T meter didn’t gave any reading! So for final solution I connected power line EMI/EMC filter with ground connected to earthing and reterminal DM screen worked correctly!

Now for final solution, I will be purchasing good quality power line EMI/EMC filters TDK make and call it a day until something comes up in future.

What’s your take on this problem? Is it a very different case of EMI/EMC or something related to quality/harmonics of AC power supply?

Hi There,

Anshuman,
That is absolutely fantastic news! I am glad to hear that adding the EMI/EMC filter completely stabilized the touchscreen. You can officially mark that down as the solution!
:grin: :+1:

To answer your question: what you are experiencing is actually a very classic case of heavy industrial EMI/RFI, rather than just a simple issue of AC ripple or power supply quality.

Because you are deployed across 19 injection molding machines with long LAN and RS485 data lines, your entire setup is essentially sitting in a massive web of high-frequency common-mode noise. This noise is generated by the massive inductive loads (like heater bands, motors, and hydraulic pumps) switching on and off.

Why the Filter Solved It:

  • The UPS Test: When you ran it on a battery UPS and the issue persisted, it proved that the noise wasn’t just coming from the AC mains into the SMPS.

  • The Real Culprit: The high-frequency noise is likely being radiated through the air or induced directly onto your communication lines and the machine’s massive metal chassis.

  • The Shunt: Capacitive touchscreens (like the one on the reTerminal-DM) are incredibly sensitive because they rely on detecting tiny changes in capacitance relative to earth ground. When you added the power line EMI/EMC filter and tied its ground to earthing, you created a low-impedance path that shunts all that high-frequency stray noise safely away to ground before it can confuse the touchscreen controller.

A Quick Tip Moving Forward:

Going with high-quality TDK filters is an excellent permanent choice—they make great industrial-grade components. When you install them permanently, just try to keep the wire runs between the TDK filter and the reTerminal-DM as short as possible. If those wires are too long, they can act like little antennas and pick up the radiated noise all over again.

Awesome troubleshooting job sticking with it and finding the root cause. Enjoy the flawless screens!

GL :slight_smile: PJ :hammer_and_wrench:

Thanks @PJ_Glasso marked this solution as solved! I hope seeedstudio can consider this in design for future upgrades in other products which are industrial environment oriented!

@PJ_Glasso back with a bit bad news, some of the reterminal DMs are not working and causing the ghost issues. I went to the factory floor and when machines were switched off including VFDs, heaters ALL THE reterminal DMs worked as intended. I gave a picture to chatgpt and visualized how EMI or noise can be causing issue. Considering this situation I am also planning to mount the reterminal DM in a 2mm steel box to shield from EMI and other noises:

Hi there,

Awesome , getting Back.. WOW that is an EYE full.
I think seeed may need to do some EMI interference testing or provide a metal casing, Very interested in the metal Box outcome. Meanwhile would be good to know is it EMI, RF or EMI on the POWER line that is the culprit. Would be keen to know for sure. can you power it in isolation (extension cord) from separate outlet ?
Is it just proximity?

Very good project for sure and a REAL world one at that… :+1:
Everyone will benefit from the findings and following. :wink:

GL :slight_smile: PJ :v:

Thanks for the great contribution.

EDIT>>>
So After some digging, you may want to consider this route too.
$15 bucs , peel and stick to the inside cover, catch at least one standoff for the connection. my be exactly what the supplier left out, for HMMI environments.
I had an Orbital welder in a fab play havoc on some unshielded sled wafer carriers, and man talk about a moving target. :grin:
would be great if you could get some measurements, RMS , spike, peak, some TDR even.
Power isolation, what about a UPS ?

Ideal Setup Recommendation

If your goal is EMI shielding and grounding behind the large 10.5-inch panel:

  1. Apply a layer of copper tape or conductive foil to the inner surface of your PLA+/TPU enclosure to create the shield ground plane.

  2. Use 3M 9703 specifically at the contact points where the E-paper display’s grounded metal bezel or PCB ground pads meet that copper foil.

  3. For mechanical mounting and shock absorption across the rest of the 10.5-inch panel, stick non-conductive double-sided acrylic foam tape (or thin EVA foam) around the border to cushion the glass substrate from flexing.

HTH
GL :slight_smile: PJ :v:

Maybe build a room like this, No :winking_face_with_tongue:


:+1:

Hi @PJ_Glasso

Thanks for your feedback. Here are the pointers:

  1. measurements, RMS , spike, peak, some TDR even. Power isolation, what about a UPS: I currently do not have EMI meter to test these values but as mentioned when all the machines are off [VFDs and heaters] all 19 reterminal DMs work correctly.
  2. Apply a layer of copper tape or conductive foil to the inner surface of your PLA+/TPU enclosure to create the shield ground plane: Currently all 19 reterminal DMs are mounted directly on DIN Rail and will try to fabricate 2mm steel box to house these.
  3. Use 3M 9703 specifically at the contact points where the E-paper display’s grounded metal bezel or PCB ground pads meet that copper foil: For reterminal DM, it is not an E-paper display, but will definitely try this approach if it makes difference.
  4. For mechanical mounting and shock absorption across the rest of the 10.5-inch panel, stick non-conductive double-sided acrylic foam tape (or thin EVA foam) around the border to cushion the glass substrate from flexing: This is not an issue for now.

@PJ_Glasso Here is the photo inside of the reTerminal-dm:

Now considering that enclosure is die-cast metal clamshell. That is a Faraday cage. Foil tape inside a metal box buys almost nothing.

For the fault - as when touching the screen it zooms in/out, no input is possible, so it might be due to DSI Flex cable.

Now for the 3M 9703, and 3M 1181 is it worth it to try out shield the DSI flex cable?

Should I directly reach to seeed technical team or you refer some workaround or trial?

Hi there,

WOW, Great lQQk on the inside, I’m running an image analysis on it now, Let’s see what the Scan reveals from the AI.
:grin:

First time I have seen the inside , A die-cast enclosure is theoretically an excellent RF/EM shield, but in practical industrial installations, it often fails to act as a proper Faraday cage for the touch controller due to ground-loop dynamics and unbonded interfaces.

Stay tunned…

I think Grounding is the issue or power isolation, one of those two would be IMO root cause.

Good stuff , thanks for following through. :+1:

GL :slight_smile: PJ :v:

Thanks @PJ_Glasso for the update. For the next step I want to close this issue with permanent fix :slight_smile:

Hi there,

So WOW… the image came back with several notes from AI YOLO scan.
The Shielding is questionable on my observation already, I added the posts to the description for the model to evaluate the whole environment.
HERE are the OUTPUTS.

Why the Die-Cast Shell Falls Short Here

  • Common-Mode Ground Shift: In an industrial cabinet with active VFDs and heaters, high switching-frequency noise ($dV/dt$) pollutes the DC ground reference. Because the touchscreen controller relies on sensing minute changes in capacitance relative to local circuit ground, a noisy floating ground makes false touches or zoom/pinch artifacts inevitable until an operator touches the chassis (acting as an earth reference).

  • Anodization & Non-Conductive Coatings: Die-cast aluminum usually features clear chromate, paint, or anodized surface finishes that create high-frequency impedance between mating halves. Without direct, metal-to-metal continuity or conductive EMI gaskets along the entire perimeter seam, high-frequency industrial noise penetrates the housing.

  • Aperture & Display Exposure: The front display aperture and touch glass itself sit outside or right at the boundary of the cavity. If the projected capacitive (PCAP) sensor ITO layer and display bezel are not bonded to a clean earth ground with low RF impedance, the enclosure cannot protect against frontal noise.

  • Internal Cable Coupling: Even with a metal shell, high-frequency ripple on the 24 V power rail couples into the internal circuitry. Shielding the DSI/I2C flex cable with grounded copper tape (3M 1181) can mitigate radiated crosstalk inside the cavity, but it will not fix conducted common-mode noise.

Actionable Steps

  • Earth the Chassis Directly: Run a dedicated, short, low-impedance ground braid from the die-cast enclosure directly to the central industrial star-ground / PE busbar, rather than relying strictly on the DIN rail clip.

  • Isolated DC Supply: Test powering the unit via a dedicated isolated DC-DC converter or an isolated 24 V supply equipped with a common-mode choke and filter directly at the terminal input.

  • Internal Cable Shielding: Wrapping the DSI/touch FPC with 3M 1181 (conductive copper tape) and terminating it to the internal PCB ground plane will help if the cable runs close to the internal DC switching regulators.

Findings:
Isolation, Isolation, then some Isolation , LOL
:grin:

WELL, I think we already arrived at this but good to know the common thread, I’ll pass on to the seeedineers and see what comes back, they should do more testing in these environments, I think the DIE-Cast was to add weight and “appearance” of Heavy duty.

Ideally it should work without the RF hoop jumping. IMO. it shows the shielding is insufficient or power supply filtering is sub par.

HTH
GL :slight_smile: PJ :v:

The TAPE over the Ribbon and super solid grounds, verified. would be my next move. :+1:

@PJ_Glasso

I will try the above options and will revert back on the same. Thanks for your feedback.

Root cause found and fixed: GT9271 touch controller ships with debounce disabled

The hardware EMI path was a dead end. The actual cause is a single configuration byte that ships with the wrong value on every unit.

TL;DR: All reTerminal DM units in our deployment shipped with shake_count = 1 in the GT9271 capacitive touch controller. shake_count is the number of consecutive scan frames a contact must persist before the controller reports a touch event. At value 1 (one frame, ~10ms), any brief capacitive coupling through the operator’s body registers as a real touch. Raising it to 4 eliminated ghost touches on all 19 units. No hardware changes needed.


What we ruled out

  • Earthing topology changes (star topology, direct PE bond): no effect
  • Bonding 24V supply negative terminal to PE: no effect
  • SAKO SAKURA EMI filter on power input: appeared to help, but units on battery UPS still showed the same behaviour, ruling out conducted power-line noise as the primary path
  • DSI flex cable shielding: not needed
  • Steel enclosure: not needed

The hands-off test was the key diagnostic. Nine minutes of capture across three units with machines running and no human contact produced zero phantom touch events. This confirms the mechanism is touch-triggered capacitive coupling through the operator’s body, not free-running EMI.


Root cause

The Goodix GT9271 stores its configuration in a 186-byte register block starting at address 0x8047. Byte offset 8 (register 0x804F) is shake_count: how many consecutive scan cycles a contact must be detected before the controller reports BTN_TOUCH. Factory value on every unit tested: 1.

At the GT9271 default 100 Hz scan rate, shake_count = 1 means a 10ms contact is sufficient to register a touch. When an operator touches the screen in front of an injection moulding machine, their body couples common-mode disturbance from heaters, hydraulic pump motors, and VFD drives into the panel for roughly 10-30ms. The controller cannot tell this from a real tap.

This is not a floating DC reference problem. It is a debounce problem. The chip ships with debounce effectively disabled.

Measurements at factory settings (shake_count = 1)

Scenario Expected Measured
Office bench, 50 deliberate taps 50 72 (+44%)
Machine 16 (heavy EMI), 120s tap test ~120 354
Machine 16, 9 min hands-off capture, machines running 0 0
Machine 16, same 120s tap test at shake_count = 4 ~120 37

The fix

The Linux mainline goodix_ts driver (used in Ubuntu Frame images on reTerminal DM) reads /lib/firmware/goodix_9271_cfg.bin at every probe and programs the chip if the file is present. The file does not exist on factory images, so the chip runs its own NVM config at shake_count = 1. Writing a modified blob to that path is all that is required.

Each unit’s config carries panel-specific calibration values. Build the modified config from that unit’s own live chip, never copy a blob between units.

Step 1: read the chip config

sudo modprobe i2c-dev
sudo python3 gt9271.py read

Reads 186 bytes live over I2C bus 10, address 0x5d. Validates checksum. Saves the factory config as a backup.

Step 2: build a modified config

sudo python3 gt9271.py make shake_count=4

Patches byte 8 in the live config, recalculates checksum using (~sum(cfg[0:184]) + 1) & 0xFF, sets config_fresh = 1, writes to /lib/firmware/goodix_9271_cfg.bin.

Step 3: reload the driver

sudo python3 gt9271.py apply

Unbinds then rebinds the Goodix-TS driver on 10-005d. Driver re-probes, reads the new file, programs the chip.

Step 4: verify

sudo python3 gt9271.py read
# expect: shake_count off 8 reg 0x804F = 4 (0x04)

Or directly without the tool:

sudo modprobe i2c-dev
i2cget -y 10 0x5d 0x4f
# factory: 0x01   after fix: 0x04

Driver note: This targets the mainline goodix_ts driver, not Seeed’s out-of-tree gt9xx. Confirm: ls /sys/bus/i2c/drivers/Goodix-TS/ should show 10-005d.


Persistence

/lib/firmware/goodix_9271_cfg.bin survives reboots. The driver reads it at every probe.

Warning: Re-imaging the OS wipes /lib/firmware/ and silently returns the unit to factory shake_count = 1. Bake the file into your standard image, or add a commissioning step to verify it after any reflash.


Results on fleet of 19 units

All 19 reTerminal DM units are now on shake_count = 4. Ghost touches eliminated across the entire fleet, confirmed by plant manager. Typing in login screens works correctly. No missed keystrokes in one week of monitoring. Changes survive reboots.

shake_count = 3 gave ~90% improvement with slightly slower touch feel reported. shake_count = 4 was required to fully eliminate ghost touches on machines with the heaviest inductive loads.


Note to Seeed

Every unit in this deployment (19 units, production ~2025-2026) shipped with shake_count = 1, the minimum possible value. The GT9271 datasheet describes shake_count as a noise rejection parameter specifically for industrial environments. A default of 3-4 would be appropriate for an industrial HMI product.

Reproducible on any quiet bench: our office unit registered 72 contacts for 50 deliberate taps at factory settings.

Quick check on any reTerminal DM:

sudo modprobe i2c-dev && i2cget -y 10 0x5d 0x4f
# 0x01 = factory default (affected)
# 0x04 = after fix

Thanks @PJ_Glasso for your continued support :slight_smile:

Hi there,
:grin:

Holly molly…

GREAT work detective… WOW! :smile:
Well. I’ll say this NO other poster has been this thorough, you chased down every inkling of a problem, double checked and Such a miniscule item turns out to be a fix.
Excellent job. Your employer should be pleased, I am. :+1:

GL :slight_smile: PJ :v:

Thanks for putting on a Clinic in this thread, We all appreciate it :saluting_face:

Thanks @PJ_Glasso for the kind words! I’m not an employee, I’m the CEO at Swayatt Drishtigochar, based out of India: https://www.swayatt.com/

Well, the customer wasn’t too happy, as it took us almost 3-4 months to figure out the issue, and we had to ship the solution quite late.

But now we’re ready to take on another problem of similar intensity in the future. Thanks again!